1 f; L& F9 h; o1 a4 i* O% A$ k4 Q/ a
Standard(s)-(year and edition):9 s3 b0 O* e5 h' ?2 `
IEC 61643-1, 2nd edition, 2005-03" q. p7 @# ^9 X5 i2 H% z( e5 r( N
Sub clause(s): 7.5 a) 7.5.4 a)
: m. A- i0 k9 U. z# vDSH- 643
( _) \8 U# T0 t' X5 \) S" S% OSubject:
9 \* ?; K6 c3 _& k% A/ xMeasured limiting voltage8 w& n+ D9 L9 m! g3 |! J0 U1 r
Key words:) |6 f+ j. _3 B+ W5 j
- measured limiting voltage2 c: T8 |' Q' n
- protection level/ T" N6 U, i+ ^7 `( P3 b7 Y% }
- energised testing
! W3 `7 l0 g- E1 X2 L5 AApproved by the 45th CTL plenary meeting 2008
D7 \, U& V3 b G3 Y, {Question:" a9 m+ \( |* F, L7 g
Testing of one port SPDs according to test class III (Type 3):/ d2 k: _- D2 O# a& b; z
Should the test to measure the limiting voltage with the combination wave be performed with the SPD being energised at Uc or without energisation?
- ^9 [+ ?. J+ w6 e8 X jRationale:8 N, C& c7 O3 m$ p7 q* ^! V
Clause 7.5 a) of the standard requires:
& e( ]9 _, g9 V: A0 QAll one-port SPDs shall be tested unenergized. …
) Z9 x; z6 z1 U! C; T+ t0 N4 yClause 7.5.4 of the standard requires:
1 \& R @: L3 w& T( Wa) The combination wave will be applied to an energized SPD, with the mains voltage at Uc.8 b7 h/ X+ v' i/ t; M5 N" k. Z6 L
As testing energised may give higher measurement results, the test should be performed energised
/ D) I( @( m5 Q4 i U' SDecision:
0 [) z+ g# f5 ]' Y& D- dThe test shall be performed with the SPD being energised at Uc.
9 O& j0 X1 z+ [& G% @0 z: c( e / H- ^+ N/ ?/ I/ s9 C1 H
+ N* z8 l- E9 C) J9 _& z: C. T5 K
|