根据60335最新版标准条款23.5最后一句, 单层内部线绝缘不提供加强绝缘:
5 l: N2 g$ W- P7 o: W2 }23.5 The insulation of internal wiring that is subjected to the supply mains voltage shall withstand the electrical stress likely to occur in normal use.
6 V2 b# z. Y( Z) E+ l o' J% F" S
& s7 ]% o {" |) wThe basic insulation shall be electrically equivalent to the basic insulation of cords complying with IEC 60227 or IEC 60245 or comply with the following electric strength test.: g X: Y9 A _/ P7 z' B' o2 \
A voltage of 2 000 V is applied for 15 min between the conductor and metal foil wrapped around the insulation. There shall be no breakdown.6 N' A5 b1 i0 A9 _: _
NOTE 1 If the basic insulation of the conductor does not fulfil one of these conditions, the conductor is considered to be bare.% C3 Q# \6 }: ?4 _/ n8 A7 B0 |( A
NOTE 2 For class II construction, the requirements for supplementary insulation and reinforced insulation apply except that the sheath of a cord complying with IEC 60227 or IEC 60245 may provide supplementary insulation.
6 ~- h' C5 n4 C" iA single layer of internal wiring insulation does not provide reinforced insulation.
- b: S. J' G/ a+ w: j9 z) Z6 k6 V3 T/ R7 {8 ^
" J) G2 R( Q4 l
8 k- H/ w# ?1 e2 P假如单层内部线绝缘的厚度达到了2mm, 也不可以当加强绝缘吗?表示极度疑惑。# Z1 A5 n! a5 @1 @, F
|
|