据本人理解, 完成 “insert” and “withdrawn” test 后, 不应用经过测试后之 ISOD plug 去做 earth resistance test (BS 1363-2, 10.2.1B), 应用 “standard rewirable plug used prior to the test”, 即 “three different makes of rewirable plugs”
- x/ ]: P- v7 h) J0 Q( |$ H. r+ C0 u$ Q% G; L% k( U
12.9.5.2 Compliance shall be checked by the following:9 N0 F9 `# D: H! P2 g- t
6 D3 X' w; ^5 m! ]
Using a selection of three different makes of rewireable plugs conforming to this standard and three different makes of unswitched socket-outlets conforming to BS 1363-2, selected to represent different earth contact designs, the earth resistance between the earthing plug pin and earthing socket contact of the socket-outlets shall be established in accordance with BS 1363-2, 10.2.1b).
2 Q) A6 O. i, S' g9 G# c: p
- J0 o6 ^7 r* q$ p0 H7 l6 S4 LAll socket outlet shall be of the type where the earth pin or ISOD of a plug inserted into the socket-outlet operates the shutter mechanism. ......4 ]6 ]/ `: Q) h# Y4 Z8 y9 y