有没有人知道如下条款中说提到的电压梯度的峰值如何检测?有没有实例说明怎么将这个条款应用到线路板上呢?谢谢!
( O/ E1 R8 m2 r/ X9 X7 L4 V% F$ A: T+ ~2 Z( B3 L
28.14 u9 J7 |$ x& j6 a; w- C7 T
For conductive patterns on printed circuit boards, except at their edges, the values in the: X1 W% a1 m% ^1 i% b
table between parts of different potential may be reduced, as long as the peak value of the
5 r5 {$ T& S* Q' jvoltage stress does not exceed:
, ]) I& @7 C2 g$ S( b- S– 150 V per mm with a minimum distance of 0,2 mm, if protected against the deposition of dirt;
% y! x8 \* n2 F' Y– 100 V per mm with a minimum distance of 0,5 mm, if not protected against the deposition of
( ^8 ~- y* [! Q1 P) cdirt.& @( D) ]. Z* l
When the limits mentioned above lead to higher values than those of the table, the values of
4 |: Z; s3 Y6 |: @$ _% L8 c+ [the table apply.4 u$ O$ K1 u9 d1 U
For peak voltages exceeding 50 V, the reduced creepage distances only apply if the Proof8 l$ |! Y6 }; q
Tracking Index (PTI) of the printed circuit board, measured as in Annex G, is greater than. H8 k' U, x. H# w
175.
5 F/ R, h$ K; i2 k8 Y! `% HThese distances may be reduced further, provided that the tool complies with the$ @9 y m3 e" H8 H" u8 z5 J
requirements of Clause 18 when the distances are short-circuited in turn.
3 h; R; O `9 X& ]+ _' n0 _- u0 A5 Q6 K0 M4 C0 z
对印刷电路板上的导电图形,其边棱除外,只要电压梯度的峰值没有超过下述值,表中关于不同极性部件间的值可以减小. 4 V1 a) n: z0 ]( M" h9 _
——若是防尘物沉积的,为150V/mm,但最小距离为0.2mm.
8 {" G4 t, ] i- T0 y- p ——若不是防尘物沉积的,为100V/mm,但最小距离为0.5mm.
3 W" P3 B- {& V! U 对峰值电压超过150V的情况,只有印刷电路板的耐漏电起痕指数(PTI)按照附录G进行测量时超过175,减小的爬电距离规定才适用.# u- y- f; @9 P9 e' F+ ]) B
只要当这些距离轮流短路时,器具符合19章的要求,这些距离可以进一步的减小. |
|